210.8(B) GFCI - industrial facility

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have an industrial building that is completely open on all four sides with general use 120VAC, (HUBBELL) duplex receptacles installed on some of the columns.
The receptacles have plastic covers BUT are not GFCI protected - nor are the branch circuit breakers GFCI. There’s no question rain will hit the receptacles at some point - they’re trying to say since it’s in an industrial facility where qualified electricians are employed it’s ok.
Is this a violation?


Sent from my iPhone using Tapatalk
 

jap

Senior Member
Occupation
Electrician
They're probably correct, although it doesn't have much to do with being a qualified person or whether or not rain would hit the receptacle.

JAP>
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
They're probably correct, although it doesn't have much to do with being a qualified person or whether or not rain would hit the receptacle.

JAP>

Where did you look in NEC to find that?


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Look at 210.8(b) (4) exception (2) . It talks about having an assured equipment grounding conductor program.

But these receptacles do not fit that description. They would not create a hazard if power is interrupted


Sent from my iPhone using Tapatalk
 

jap

Senior Member
Occupation
Electrician
What code cycle are you all basing the violation off of?

JAP>
 

jap

Senior Member
Occupation
Electrician
Looks like a violation to me. Sounds like an indoor wet location...210.8(B)(6)

Sound like an outdoor car port type structure to me at an industrial plant.

At one time GFI protection was not required for that, but, things may have changed.

JAP>
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Sound like an outdoor car port type structure to me at an industrial plant.

At one time GFI protection was not required for that, but, things may have changed.

JAP>

This is not for a carport installation.


Sent from my iPhone using Tapatalk
 