I have a coffee maker. 208v single phase more than 6 feet away from a sink. it is a commercial kitchen. 30 Amp. does it require a GFI breaker?
210.8(B) Other Than Dwelling Units.
All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts
or less to ground, 100 amperes or less, installed in the locations specified in 210.8(B)(1) through (B)(12) shall have ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Kitchens or areas with a sink and permanent provisions for either food preparation or cooking
I’m on code 2017. Did this change in 2020?Yes,