Is there anything that would require GFCI protected receptacles in the attics of a dwelling unit?
Is there anything that would require GFCI protected receptacles in the attics of a dwelling unit?
Thanks. Yes, unfinished.
2-50 Log #2390 NEC-P02
(210-8(A)(9) (New) )
Final Action: Reject
Submitter: Terry L. Schneider, Pikes Peak Regional Building Department
Recommendation:
Add new item (9) Attic spaces.
Substantiation:
When the outlet is installed in attic spaces, it is usually for equipment, such as furnaces, with duct work and other grounded material.
These present a shock hazard, that along with the potential temperatures, can easily produce death. Two electricians in Colorado have
died when laying over duct work and coming in contact with a hot wire. The hazard makes it very difficult to get remove your body if
muscle lock occurs during the shock.
Panel Meeting Action: Reject
Panel Statement:
The submitter should supply more specific information on the incidents cited so that the panel can better understand the issue. There is
no indication that the electrocutions occurred from the installed outlet, or from some other source.
Number Eligible to Vote: 13
Affirmative: 13
No, it services a fan for a bathroom vent pipe.Is an air handler nearby in this attic?
210.63 requires a receptacle within 25 feet but it doesn't have to be GFI.
Is there anything that would require GFCI protected receptacles in the attics of a dwelling unit?
Not yet.