210.8B GFCI and commercial kitchens and water heaters
dm9289
Industrial Maintenance Electrician
Pennsylvania
Industrial process repair/ maintenance Electrician
In looking thru code mostly 210.8B and 422 I have some confusion about GFCI protection
It seems to basically say all things in a commercial kitchen. Would a walk-in cooler be part of a commercial kitchen? As i read I imagine a typical residential fridge in residential no GFCI but same fridge in commercial probably yes.
Or would a residential or commercial hot water tank require GFCI protection? I can see no requirement. I believe it needs GFCI but I cannot find in code
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
If they are direct wired then no gfci is necessary.
(B) Other Than Dwelling Units.
All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts or less to ground, 100 amperes or less, installed in the locations specified in 210.8(B)(1) through (B)(12) shall have ground-fault circuit-interrupter protection for personnel.
Dennis Alwon
Chapel Hill, NC
Thats odd to me seems like a safety work around cause am I correct in assuming same hazards exist.
I believe the reason for the receptacles to be gfci protected is because of their tendency to break down and loosen up connections, especially the ground. Less likely to happen with a direct wire
jap
And, if you mention the word "outlet" and GFI in the same sentence around here it's going to cause a storm of responses... :)
JAP>
dm9289
Pennsylvania
Makes more sense now
JAP>
You are correct as usual sorry GFCI receptacle lol. The verbiage is important.
Little Bill
Tennessee NEC:2017
Semi-Retired Electrician
They often move equipment for cleaning, and if they move them farther than the cord allows, they have to unplug them. That's one of the reasons for the GFCI.