From the 2020 NEC:210.8(D) Kitchen Dishwasher Branch Circuit. GFCI protection shall be provided for outlets that supply dishwashers installed in dwelling unit locations
210.8(D) Specific Appliances. Unless GFCI protection is provided in accordance with 422.5(B)(3) through (B)(5), the outlets supplying the appliances specified in 422.5(A) shall have GFCI protection in accordance with 422.5(B)(1) or (B)(2).
Just curious, how is that different than the 2017 requirement in 210.8(D)?Note that 422.5 (A)(7) requires dishwashers to be protected by GFCI whether they are connected by cord and plug or hardwired. This is new for the 2020 code.
Requirements have not changed. Location in code and maybe a little different wordsmithing is all that really changed.Just curious, how is that different than the 2017 requirement in 210.8(D)?
Do you agree that the 2017 NEC required GFCI protection for dishwashers? It sounds like you're saying that didn't appear in the NEC until the 2020.Residential dishwashers historically have escaped GFCI protection in earlier revisions of the code. The operative changes were around 2011 version of the code which made a receptacle within 6' of a sink required it, even in kitchens. Otherwise, unless you plugged it in on the countertop, GFCI wasn't mandated.
In the 2014 code and earlier. Article 422 (Appliances) spread the GFCI requirements out with the particular appliances: tire inflation and automotive vacuum machines for public use, high-pressure spray washers, vending machines, and drinking fountains. The 2017 code relocated these five items into 422.5 while also coalescing the various things about plug-mounted GFCIs and the like that was scattered throughout the article as well.
2020 added sump pumps and dishwashers to the list.
That is the case to my understanding. Unless your dishwasher happened to be plugged into a receptacle otherwise covered by 210.8, there was no strict requirement to have GFCI protection until 422.5 was changed in the 2020 code. The relocation I believe Kwired is referring predates the addition of the dishwasher requirement.
It was added in the 2014 NEC, reference is in post #2.That is the case to my understanding. Unless your dishwasher happened to be plugged into a receptacle otherwise covered by 210.8, there was no strict requirement to have GFCI protection until 422.5 was changed in the 2020 code. The relocation I believe Kwired is referring predates the addition of the dishwasher requirement.
Actually 210.8(D) was new in the 2014 code.It was added in the 2017 NEC, reference is in post #2.
One of the issues is far too many code users do not understand the meaning of "outlet" and read it as "receptacle".(D) Kitchen Dishwasher Branch Circuit.
GFCI protection shall be provided for outlets that supply dishwashers installed in dwelling unit locations.
Actually 210.8(D) was new in the 2014 code.
Dennis pointed out you did have a local amendment that did not recognize a change that happened in 2014 involving GFCI protection of dishwashers. Actual NEC did require GFCI protection of dishwashers in dwelling units in 2014 in section 210.8. The reason wasn't as much for shock/electrocution prevention as is the reason for nearly all other GFCI rules but rather an issue with a component failure on many models that was starting fires, GFCI's happened to be responding to this failure. Whole thing should have been CPSC forcing a recall and have the manufacturers of these appliances fix the issue, instead they found a way to convince NEC to put this requirement in.That is the case to my understanding. Unless your dishwasher happened to be plugged into a receptacle otherwise covered by 210.8, there was no strict requirement to have GFCI protection until 422.5 was changed in the 2020 code. The relocation I believe Kwired is referring predates the addition of the dishwasher requirement.