This may be a little off target with the OP's question but I will present it anyway.
I suggest reading art. 310.15(B)(6) very carefully. Here is what I understand it says I can do.
Scenario: Single family dwelling--One meter with 2 - 200 amp discos (400 amp service). The disco has feed thru lugs for 200 amps and 2- 200 amp sub panels are added inside the building.
The wires between the meter and the discos can be 2/0 copper since Table 310.15(B)(6) allows that for single family dwelling. My reason is that since the conductors between the meter and the main disco are service entrance conductors, art. 310.15(B)(6) states can use T310.15(B)(6).
Now what size copper conductors, in conduit, must I install from the main disco to the interior panel? Let's assume 90 C conductors --- anyone want to bite at this one.....