Quick check please. A 225 amp breaker in a distribution panel feeds an overhead plug-in busway in a new lab building. The busway is rated 225 amps. None of the equipment to be eventually plugged in has been selected yet. So I calculated the KVA equivalent of three phase, 225 amps, divided it by 3, and put that value on each phase of the panel schedule as the busway load. The client is now telling me that I should have multiplied this value by 80%, because of the 80% rating of the breaker. My view is that the total load (all 225 amps) represents 100% of the non-continuous load plus 125% of the continuous load, and that I can therefore show (on the panel schedule) a load of 100% of the breaker's rating.
What say ye?
(I will probably do what the client wants anyway, but I prefer knowing that I was right-if indeed I was right.)
What say ye?