I touched on this issue in an earlier post along with other issues related to this design method back in Oct.
http://forums.mikeholt.com/showthread.php?t=179824
Spanked thoroughly, but would like to resurrect discussion on this specific article.
The basic design scheme...multi-family 120/208v-3p-4w service with each apartment served 3W, nothing new here.
Design provides for 4W risers to serve 3, 4, 5 or six apartment. NEC does not cap the number, these are numbers from plans I have seen installed.
Each apartment is served via 3W tap from the 4W riser. Metering achieved electronically (CT's).
The push back was that this article would not apply because the riser is a 4W feeder, and each tap is a separate feeder and therefore NO sharing of a common neutral.
My claim was the neutral could be simply looped up the riser, source - pnl - pnl - etc and this would help visualize these feeders are in fact sharing a common neutral.
I have recently ran multiple electronic circuit models of both designs with identical loads and in every case the neutral current along the neutral for each design is the same +/- .5amp as compared to a design of separate phase conductors, six sets...a-b, b-c, c-a, etc + common neutral up the riser.
The point being if the writers intention is to put limitations on this design method, I am assuming because of specifically the potential to overload the neutral.
Help me get this out of my head.
http://forums.mikeholt.com/showthread.php?t=179824
Spanked thoroughly, but would like to resurrect discussion on this specific article.
The basic design scheme...multi-family 120/208v-3p-4w service with each apartment served 3W, nothing new here.
Design provides for 4W risers to serve 3, 4, 5 or six apartment. NEC does not cap the number, these are numbers from plans I have seen installed.
Each apartment is served via 3W tap from the 4W riser. Metering achieved electronically (CT's).
The push back was that this article would not apply because the riser is a 4W feeder, and each tap is a separate feeder and therefore NO sharing of a common neutral.
My claim was the neutral could be simply looped up the riser, source - pnl - pnl - etc and this would help visualize these feeders are in fact sharing a common neutral.
I have recently ran multiple electronic circuit models of both designs with identical loads and in every case the neutral current along the neutral for each design is the same +/- .5amp as compared to a design of separate phase conductors, six sets...a-b, b-c, c-a, etc + common neutral up the riser.
The point being if the writers intention is to put limitations on this design method, I am assuming because of specifically the potential to overload the neutral.
Help me get this out of my head.