pete m. Senior Member Location Ohio Dec 8, 2006 #1 Looking for opinions....... In relation to the code section in the title what would constitute a "five-wire" feeder? Secondly, would the neutral or grounded conductor be counted as one of the five wires? Thanks, Pete
Looking for opinions....... In relation to the code section in the title what would constitute a "five-wire" feeder? Secondly, would the neutral or grounded conductor be counted as one of the five wires? Thanks, Pete
R RB1 Senior Member Dec 8, 2006 #2 I believe the reference is to a two-phase, five wire feeder with four of the wires being ungrounded and one of the wires being grounded.
I believe the reference is to a two-phase, five wire feeder with four of the wires being ungrounded and one of the wires being grounded.