Is this allowed by code? Not would you do it, however is it allowed?
Assume 200AMP service.
Assume disconnect properly installed outside.
3 wire 4/0, 4/0, 4/0 ran to “sub” (main) panel.
Bare copper ran for equipment grounding for this panel to disconnect.
Before you respond read the following.
Note the “”.
215.6 Feeder Conductor Grounding Means. *****, the feeder shall include “or” provide a grounding means,******
Note: using the 250.134 reference.
250.134****, shall be grounded by one of the following methods.
250.134(A) Equipment Grounding Conductor Types. By “any” of the equipment grounding conductors permitted by 250.118.
250.118 Types of Equipment Grounding Conductors. The equipment grounding conductors “with” “ or” enclosing the circuit conductors shall be “one” or more or a combination of the following.
250.118(1) A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be “solid” or stranded; insulated, coved, or “bare”; and in the form of a “wire” or a busbar of any shape.
Does "with" mean outside of the cable, or does it mean "in" the cable?
Other code references usually state "contained witin the same raceway or cable".
Mike P.
Assume 200AMP service.
Assume disconnect properly installed outside.
3 wire 4/0, 4/0, 4/0 ran to “sub” (main) panel.
Bare copper ran for equipment grounding for this panel to disconnect.
Before you respond read the following.
Note the “”.
215.6 Feeder Conductor Grounding Means. *****, the feeder shall include “or” provide a grounding means,******
Note: using the 250.134 reference.
250.134****, shall be grounded by one of the following methods.
250.134(A) Equipment Grounding Conductor Types. By “any” of the equipment grounding conductors permitted by 250.118.
250.118 Types of Equipment Grounding Conductors. The equipment grounding conductors “with” “ or” enclosing the circuit conductors shall be “one” or more or a combination of the following.
250.118(1) A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be “solid” or stranded; insulated, coved, or “bare”; and in the form of a “wire” or a busbar of any shape.
Does "with" mean outside of the cable, or does it mean "in" the cable?
Other code references usually state "contained witin the same raceway or cable".
Mike P.