215.8

Status
Not open for further replies.

eric stromberg

Senior Member
Location
Texas
In the 2002 Code, 215.8 mandated the use of an orange wire for the high leg of a 240/120 three phase (delta) system.

215.8 is gone in the 2005 Code. Where did it go? Is there still a requirement for the high leg to be orange? If so, where?

Thanks,

Eric
 
408.3 [With some commentary NEC 2005 Handbook]

(E) Phase Arrangement The phase arrangement on 3-phase buses shall be A, B, C from front to back, top to bottom, or left to right, as viewed from the front of the switchboard or panelboard. The B phase shall be that phase having the higher voltage to ground on 3-phase, 4-wire, delta-connected systems. Other busbar arrangements shall be permitted for additions to existing installations and shall be marked.

The high leg is common on a 240/120-volt, 3-phase, 4-wire delta system. It is typically designated as ``B phase.'' Section 110.15 requires the high-leg marking to be the color orange or other similar effective means of identification. Electricians should always test each phase to ground with suitable equipment in order to know exactly where this high leg is located in the system.
\
The exception to 408.3(E) permits the phase leg having the higher voltage to ground to be located at the right-hand position (C phase), making it unnecessary to transpose the panelboard or switchboard busbar arrangement ahead of and beyond a metering compartment. The exception recognizes the fact that metering compartments have been standardized with the high leg at the right position (C phase) rather than in the center on B phase.

See also 110.15 and 230.56 for further information on identifying conductors with the higher voltage to ground. Other busbar arrangements for making additions to existing installations are permitted by 408.3(E).
Exception: Equipment within the same single section or bmultisection switchboard or panelboard as the meter on 3-phase, 4-wire, delta-connected systems shall be permitted to have the same phase configuration as the metering equipment.

FPN: See 110.15 for requirements on marking the busbar or phase conductor having the higher voltage to ground where supplied from a 4-wire, delta-connected system.

Exception: Equipment within the same single section or bmultisection switchboard or panelboard as the meter on 3-phase, 4-wire, delta-connected systems shall be permitted to have the same phase configuration as the metering equipment.
 