If you have a 100amp 240v 22 space panel can you have 22 20amp circuits?
I recently installed a panel with 100 amp main, 2 100 amp 2 pole branch breakers, 1 20 amp single pole and 2 15 amp single pole breakers. The load should never exceed about 60 or 70 amps from this panel though.
That could be a violation. Many panels have a maximum branch circuit breaker size and or max breaker sum per stab. Many EC realize this and wonder why the buss burned up. The information is usually on the label. I know that many GE panels have a max of 75 amp in their 100 load centers. We as EC must obide by the listing and not what we think is ok.
In most cases you go by the calculated connected load not the sum of the breakers.
Good question.