220.12 and Informational Note

Status
Not open for further replies.

fmtjfw

Senior Member
Section/Paragraph: 220.12 and Informational Note

Deleted Text

220.12 Lighting Load for Specified Occupancies.
A unit load of not less than that specified in Table 220.12 for occupancies specified therein shall constitute the minimum lighting load. The floor area for each floor shall be calculated from the outside dimensions of the building, dwelling unit, or other area involved. For dwelling units, the calculated floor area shall not include open porches, garages, or unused or unfinished spaces not adaptable for future use.

Informational Note: The unit values herein are based on minimum load conditions and 100 percent power factor and may not provide sufficient capacity for the installation contemplated.

Substantiation:

"therein" and "herein" are archaic terms which is considered to reduce clarity according to NEC_StyleManual_2011.pdf 3.3.4.

Inserted Deleted
 