X xformer Senior Member Location Dallas, Tx Occupation Master Electrician Sep 14, 2023 #1 220.14(D) - Doesn't this code section cause lights for dwelling units to be calculated twice according to the 2023 code?
220.14(D) - Doesn't this code section cause lights for dwelling units to be calculated twice according to the 2023 code?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Sep 14, 2023 #2 Not really...that is for the calculation of the branch circuit loads and not the service or feeder load for the dwelling unit.
Not really...that is for the calculation of the branch circuit loads and not the service or feeder load for the dwelling unit.
X xformer Senior Member Location Dallas, Tx Occupation Master Electrician Sep 14, 2023 #3 Thanks Don.