Is this section only referring to the required receptacle outlets of 210.62 or is it including hardwired lights?
The way I understand this is that if I had hardwired light in addition to the 210.62 required receptacles, the 200 VA per foot or 180VA per outlet called out in 220.14(G) would be added to the 200VA per foot for lights of 220.46.
Example: 10' of show window with hardwired lights and (2) required receptacles.
10x200 = 2000VA lighting load (220.46)
2 receptacles (required by 210.62) 180 x 2 = 360VA receptacle load.
Total show window load = 2360 VA