Hi, Charlie. Thanks for your reply. I am not sure if I understand you correctly.Originally posted by charlie b:
Suppose for example that the total VA/ft2 was 30. You add the following:
3 VA/ft2 at 100 % equals 3.
17 VA/ft2 (i.e., from 3 to 20) at 75 % equals 12.75.
10 VA/ft2 (i.e., from 20 to 30) at 25 % equals 2.5.
Total VA/ft2 equals 18.25.
The last two steps are to multiply the 18.25 times the total square foot, to get the total VA, and then to divide by voltage, to get amps.