Is there any reason that (in annex D, example D1a ) they apply the 35% to calculate the net calculated load but DO NOT apply 35% to calculate the feeder neutral load?
(when I say "apply 35%" I mean they take the first 3000 VA at 100% and remainder at 35% (of the general lighting, small appliance, and laundry combined VA).)
The reason I ask is because I noticed that they DID apply the 35% to calculate the feeder neutral load in example D2a!
(when I say "apply 35%" I mean they take the first 3000 VA at 100% and remainder at 35% (of the general lighting, small appliance, and laundry combined VA).)
The reason I ask is because I noticed that they DID apply the 35% to calculate the feeder neutral load in example D2a!