I'm currently looking at 220.43(B) in the 2020 NEC handbook and in the code it states that
While I see the point of rounding up, wouldn't this conflict w/ the wording in the code when it says "or fraction thereof", therefore allowing for the calculation to not be rounded?
Thanks,
- InkRF
In the handbook, there is a sample calculation for a 63ft track light, where once divided by 2 ft, the quotient is 31.50, which is then rounded up to 32.For track lighting in other than dwelling units or guest rooms or guest suites of hotels or motels, an additional load of 150 volt-amperes shall be included for every 600 mm (2ft) of lighting track or fraction thereof. Where multicircuit track is installed, the load shall be considered to be divided equally between the track circuits.
While I see the point of rounding up, wouldn't this conflict w/ the wording in the code when it says "or fraction thereof", therefore allowing for the calculation to not be rounded?