Here is a question i seem to be having a little trouble with. If anyone could help pls..
How many 120v 20a 2-wire branch circuits are required for an office area that measures 43'x80' with an unknown receptacle outlet load? Receptacles and lighting are not permitted onthe same branch circuit for this installation.
a) 6
b) 7
c) 8
d) 9
My math..
43x80x3.5=12040 t.220.44=> 10000+(2040x.50)=11020
120vx20a=2400 11020/2400=4.59 x 2 = 9.18==> 10 circuits
Do I not round down... I was sure that we round up on number of circuits.....
or do i not mutiply by 2 and find 4 mandatory outlets in art. 210.
thanks