220.44 question

Status
Not open for further replies.

patsfan51

Member
Here is a question i seem to be having a little trouble with. If anyone could help pls..

How many 120v 20a 2-wire branch circuits are required for an office area that measures 43'x80' with an unknown receptacle outlet load? Receptacles and lighting are not permitted onthe same branch circuit for this installation.
a) 6
b) 7
c) 8
d) 9

My math..
43x80x3.5=12040 t.220.44=> 10000+(2040x.50)=11020
120vx20a=2400 11020/2400=4.59 x 2 = 9.18==> 10 circuits

Do I not round down... I was sure that we round up on number of circuits.....
or do i not mutiply by 2 and find 4 mandatory outlets in art. 210.

thanks
 

Volta

Senior Member
Location
Columbus, Ohio
Here is a question i seem to be having a little trouble with. If anyone could help pls..

How many 120v 20a 2-wire branch circuits are required for an office area that measures 43'x80' with an unknown receptacle outlet load? Receptacles and lighting are not permitted onthe same branch circuit for this installation.
a) 6
b) 7
c) 8
d) 9

My math..
43x80x3.5=12040 t.220.44=> 10000+(2040x.50)=11020
120vx20a=2400 11020/2400=4.59 x 2 = 9.18==> 10 circuits

Do I not round down... I was sure that we round up on number of circuits.....
or do i not mutiply by 2 and find 4 mandatory outlets in art. 210.

thanks
Given the text of the question, should you be looking at 220.44 at all?

Maybe start it again at 220.12 and 220.14.:)
 

patsfan51

Member
the way that i read 220.14 (I) would be 180va per outlet. that would be for known outlet loads.220.14 (K) at 1va/sqft. One va per square foot throws my math off. And if the 3.5va for offices is for general lighting where would I begin....

not sure what you mean by finding the lighting load to get the receptacle load when question says not on same circuit.
 

jumper

Senior Member
the way that i read 220.14 (I) would be 180va per outlet. that would be for known outlet loads.220.14 (K) at 1va/sqft. One va per square foot throws my math off. And if the 3.5va for offices is for general lighting where would I begin....

not sure what you mean by finding the lighting load to get the receptacle load when question says not on same circuit.

Your lighting load is 12040 and your rec. is based on 1va/ sqft. Forget about 180va per rec. you do not know how many recs. Now apply T 220.42 to lights and T220.44 to recs.
 

patsfan51

Member
total load minus lighting is recept. load?
lighting:
12040-3000=9040x.35=3164+3000=6164va
recep.:
12040-6164=5878va

??????
 

jumper

Senior Member
Okay, here is what I come up with:
Lights
12040va@ 100%=12040va
12040va/120v=100.1666667a
100.16666667a=100a 220.5(B)
100a=5 circuits

Recs
43*80=3440
3440* 1va=3440va @ 100%
3440va/120v=28.66667a or 29a
29a=2 circuits

7 circuits if I am correct.
 

patsfan51

Member
ah ha!
but office lighting should be at 125% no?

12040x1.25=15050
15050/120=125.4
125/20=6.25
7 circuits for lighting
2 circuits for recept.
9 total?
 

jumper

Senior Member
ah ha!
but office lighting should be at 125% no?

12040x1.25=15050
15050/120=125.4
125/20=6.25
7 circuits for lighting
2 circuits for recept.
9 total?

Are using 210.19(A)(1) for that 125%, because I believe that should apply to the conductors. #12 is good for 25 amps. 25*.8=20 or 20*1.25=25. I am back to 7 circuits, unless I missed something else
 

jumper

Senior Member
ah ha!
but office lighting should be at 125% no?

12040x1.25=15050
15050/120=125.4
125/20=6.25
7 circuits for lighting
2 circuits for recept.
9 total?

Correct I think

Are using 210.19(A)(1) for that 125%, because I believe that should apply to the conductors. #12 is good for 25 amps. 25*.8=20 or 20*1.25=25. I am back to 7 circuits, unless I missed something else
I was wrong. I missed 210.20, thanks Volta:), 9 is the right answer, I think.
 