N normbac Senior Member Jul 17, 2008 #1 I am prewiring for a double oven the specs state electric rating 8.9 kw @ 240 Due I consider this a single appliance or 2 and would I have to use column b 8900 x 65% = 5785 240 = 24.1 that smells wrong Tia
I am prewiring for a double oven the specs state electric rating 8.9 kw @ 240 Due I consider this a single appliance or 2 and would I have to use column b 8900 x 65% = 5785 240 = 24.1 that smells wrong Tia
J JES2727 Senior Member Location NJ Jul 17, 2008 #2 It's just one connection, right? That would make it a single appliance, IMO.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jul 17, 2008 #3 If this is a resi job then you would use T220.55. Since your range is over 8 3/4 KW you must look at col. C. Col. C says maximum demand is 8KW
If this is a resi job then you would use T220.55. Since your range is over 8 3/4 KW you must look at col. C. Col. C says maximum demand is 8KW