From what I am seeing it appears you can run a 50 amp branch circuit if you have 2 cooking units of say 27 amps and 20 amps. You can tap off the 50 amp circuit and run smaller size wires not below #12 to each piece of equipment.
I understand if there is a direct gnd fault or short on either cooking unit the 50 amp breaker in panel would trip, but if you have an overload in one of the cooking units would there be a risk of fire hazard example 20 amp unit drawing 35 amps?
I don't get how this is OK im likely misunderstanding something
I understand if there is a direct gnd fault or short on either cooking unit the 50 amp breaker in panel would trip, but if you have an overload in one of the cooking units would there be a risk of fire hazard example 20 amp unit drawing 35 amps?
I don't get how this is OK im likely misunderstanding something