220.56 Kitchen Equipment

cppoly

Senior Member
Location
New York
This section gives demand factors for commercial electric cooking equipment, dishwasher booster heaters, water heaters, and other kitchen equipment.

Would you say other equipment such as refrigerators, microwaves, etc. in area can also have this demand factor applied?

What about if this equipment (refrigerator, microwave, etc.) is in pantry and not a commercial kitchen?

Thanks
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
Is this for a commercial kitchen or for a residential? They are different sections in Art. 220.

P.S. Update the occupation.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
The text of 2023 NEC 220.56 is below. Based on the wording, I would say that the only restriction on the location of the equipment is that it not be within a dwelling unit, no requirement to actually be in a kitchen.

Cheers, Wayne

2023 NEC said:
220.56 Kitchen Equipment - Other Than Dwelling Unit(s)

Calculating the load for commercial electric cooking equipment, dishwasher booster heaters, water heaters, and other kitchen equipment in accordance with Table 220.56 shall be permitted. Other kitchen equipment shall include equipment that is fastened in place and rated 1/4 hp or greater, or 500 watts or greater. These demand factors shall be applied to all equipment that has either thermostatic control or intermittent use as kitchen equipment. These demand factors shall not apply to space-heating, ventilating, or air-conditioning equipment.

However, in no case shall the feeder or service calculated load be less than the sum of the largest two kitchen equipment loads.

Table 220.56 Demand Factors for Kitchen Equipment - Other Than Dwelling Unit(s)
Number of Units of Equipment Demand Factor (%)
1 100
2 100
3 90
4 80
5 70
6 and over 65
 

cppoly

Senior Member
Location
New York
Is this for a commercial kitchen or for a residential? They are different sections in Art. 220.

P.S. Update the occupation.

It's a kitchen in a commercial occupancy. Although, when I think "commercial kitchen", I'm thinking of a kitchen in a restaurant.

But is the commercial kitchen simply comparing a commercial occupancy to a dwelling occupancy?
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
It's a kitchen in a commercial occupancy. Although, when I think "commercial kitchen", I'm thinking of a kitchen in a restaurant.

But is the commercial kitchen simply comparing a commercial occupancy to a dwelling occupancy?

I am not sure I understand the question.

If, for all intents and purposes you are designing a break room with a kitchen in it, then it seems like you should use 220.56.

If you are designing a factory where rooms are used to cook or make large quantities or pre-cooked foods (i.e. prepackaged donuts or chicken tenders) then I would advise taking a deeper dive into the different equipment being used.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It's a kitchen in a commercial occupancy. Although, when I think "commercial kitchen", I'm thinking of a kitchen in a restaurant.

But is the commercial kitchen simply comparing a commercial occupancy to a dwelling occupancy?
I believe it is as simple as that. If it isn't in a dwelling then it cannot use 220.55 but can use 220.56

There is an exception to that if the ranges are in instructional programs (note 7)
 