Nathanael47
Member
- Location
- Berkeley, California
- Occupation
- Electrician
The concept of noncoincident loads laid out in 220.60 makes a lot of sense: If you have two loads that will never be on at the same time – like a heater and an air conditioner – you only need to count the larger of the two.
However, the final sentence seems to contradict what I just said:
“If a motor or air-conditioning load is part of the noncoincident load and NOT the largest of the noncoincident loads, 125 percent of either the motor load or air-conditioning load, whichever is larger, shall be used in the calculation.”
So take the example above: an HVAC load with air-conditioning and a heat strip. Assume the resistance heat is the larger load. The sentence quoted above says now we need to include 125% of the AC load as well right?
That doesn't make any sense to me.
However, the final sentence seems to contradict what I just said:
“If a motor or air-conditioning load is part of the noncoincident load and NOT the largest of the noncoincident loads, 125 percent of either the motor load or air-conditioning load, whichever is larger, shall be used in the calculation.”
So take the example above: an HVAC load with air-conditioning and a heat strip. Assume the resistance heat is the larger load. The sentence quoted above says now we need to include 125% of the AC load as well right?
That doesn't make any sense to me.