220.61 35% Harmonic Load 120/208V 3 Phase Reduced Neutral

Status
Not open for further replies.

dmouz

Member
Some references say no reduced neutral - McPartland-
Handbook say's "a majority of the load is harmonic"

To Allow? or Not to Allow?

Maybe the code should read "Any 120 volt loads"
 

wirenut1980

Senior Member
Location
Plainfield, IN
Is the 35% harmonic load all or mostly third? Is the 35% from a specification sheet? What type of load is it? Remember that triplen harmonics add in the neutral. If I were in your shoes, I would probably try and do a quick estimate the harmonic magnitude if the loads are known, and try to get more data about the loads.

On a total wag (not recommended) if all someone told me was 35% harmonic loads, I would specify a full size neutral.
 

dmouz

Member
220.61 35% Harmonic Load 102/208V 3 Phase Reduced Neutral

220.61 35% Harmonic Load 102/208V 3 Phase Reduced Neutral

The engineer did break it out with quite a bit of detail, and the 35% represents the inductive lighting load. He can't fit a full sized neutral in the existing conduit. But it's only 5 feet from the building, so I'm not too sympathetic. His calculations are correct, but omitted some show window recpt.
I denied it, but i was looking for any one with additional practical experience. It was the 1st reduced neutral proposal I had seen in about 10 years.
The "Basic Calculation" in 220.61.A was correct, (based on continuious and non-continuious) and the neutral load, around 120 amps. The rest of the load was mostly for refridgeration and general use recpt's. The engineer did a good job of analysis.
It's a grocery store, so I figured they would have the possibility of addtional inductive signs and lighting for the display windows,,,,(christmas lights, etc.)

Anyway, I was also trying to remember back, to what edition the code changed, and allowed, "one or two" down sized neutral. back in the 220-22 days! I can't remember that article number.
 

wirenut1980

Senior Member
Location
Plainfield, IN
If the engineer calculated the neutral current based on the lighting and it was within the ampacity of the neutral, I feel better about the downsized neutral. But you still don't know what will be plugged into the general use receptacles. Given that it is a grocery store, I would feel ok with a down-sized neutral. But keep one question in mind...who's butt is going to be on the line if there are problems with over-heating due to harmonics in the future? Yours, the engineer's, or both?
 