220.61 35% Harmonic Load 102/208V 3 Phase Reduced Neutral
220.61 35% Harmonic Load 102/208V 3 Phase Reduced Neutral
The engineer did break it out with quite a bit of detail, and the 35% represents the inductive lighting load. He can't fit a full sized neutral in the existing conduit. But it's only 5 feet from the building, so I'm not too sympathetic. His calculations are correct, but omitted some show window recpt.
I denied it, but i was looking for any one with additional practical experience. It was the 1st reduced neutral proposal I had seen in about 10 years.
The "Basic Calculation" in 220.61.A was correct, (based on continuious and non-continuious) and the neutral load, around 120 amps. The rest of the load was mostly for refridgeration and general use recpt's. The engineer did a good job of analysis.
It's a grocery store, so I figured they would have the possibility of addtional inductive signs and lighting for the display windows,,,,(christmas lights, etc.)
Anyway, I was also trying to remember back, to what edition the code changed, and allowed, "one or two" down sized neutral. back in the 220-22 days! I can't remember that article number.