I see there is a conflict between these two sections for neutral sizing, am i missing something here?
(C) Prohibited Reductions. There shall be no reduction of
the neutral or grounded conductor capacity applied to the
amount in 220.61(C)(1), or portion of the amount in (C)(2),
from that determined by the basic calculation:
(1) Any portion of a 3-wire circuit consisting of 2 ungrounded
conductors and the neutral conductor of a 4-wire,
3-phase, wye-connected system
(2) That portion consisting of nonlinear loads supplied from
a 4-wire, wye-connected, 3-phase system
(1) Sizing for a Single Raceway or Cable. The grounded
conductor shall not be smaller than specified in Table
250.102(C)(1).
That's may be unintentional mistakeWhy not try and explain what the conflict is that you see.
So, full neutral is applicable for non-linear loads only?Here is what 220.61(C) states. It is talking about circuits where there are 2 hots and a neutral on a 3 phase system (wye) and a circuit that has non linear loads...
Section 250.24(C)(1) is talking about the smallest size of a grounded conductor. Obviously if the neutral (grounded conductor meets the criteria in 220.61(C) then you cannot reduce the neutral