220.82- 120/208v question

Status
Not open for further replies.

catfishdon

New User
Location
Baton Rouge La
Occupation
Elect Contractor
Gentlemen
When using this method and my main service coming in is single phase 120/208v , at the end of the calculation do we still divide the watts by 240v ? or a lesser voltage
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
No you would divide by 208v unless it was 3 phase then it would divided by 360v. Since you have single phase then it is divided by 208v
 