Now that we can view all the proposals I just came across this one Public Input No. 2407-NFPA 70-2023 from Generac of all people that proposed to treat EVSE loads differently in the residential Optional Calc.
A dwelling could have any number of large loads that run 3 hours or more and the optional calcs have historically taken that into account by where they set the demand factor cut off (10kw).
Mike has a different proposal 3204-NFPA 70-2023 [ Section No. 220.82(B) ]
That would lump EVSE's under B(3) and continue to allow the EVSE to be considered in the demand factor.
There are also a few other interesting proposals for 220.82 (and others in 220) such as 3239-NFPA 70-2023 [ Section No. 220.82(B) ]
from Lawrence Berkley National Labs (LBNL) that has been studying the effects of LED lighting on residential demand:
It is curious to me what is different about a EVSE load than any other residential continuous load?The 2023 version of NFPA 70 (NEC) article 220, Part VI - Optional Feeder and Service Load Calculations in article 220.82 Dwelling Unit, paragraphs (A), (B), and (C) currently do not specifically address the inclusion of EVSE equipment loads. This proposes a revision of article 220.82(A) to include adding a new paragraph (D) which is to include EVSE loads into the Optional Feeder and Service Load Calculation – This corresponds with Public Input No. 2282-NFPA 70-2023. Per 2023 NEC Article 220, Part III. Feeder and Service Load Calculations: • Article 220.53 Appliance Load – Dwelling Unit(s). This demand factor shall not apply to: (5) Electric Vehicle Supply Equipment (EVSE). • Article 220.57 Electric Vehicle Supply Equipment (EVSE) Load. The EVSE load shall be calculated at either 7200 watts (volt-amperes) or the nameplate rating of the equipment, whichever is larger.
A dwelling could have any number of large loads that run 3 hours or more and the optional calcs have historically taken that into account by where they set the demand factor cut off (10kw).
Mike has a different proposal 3204-NFPA 70-2023 [ Section No. 220.82(B) ]
That would lump EVSE's under B(3) and continue to allow the EVSE to be considered in the demand factor.
There are also a few other interesting proposals for 220.82 (and others in 220) such as 3239-NFPA 70-2023 [ Section No. 220.82(B) ]
from Lawrence Berkley National Labs (LBNL) that has been studying the effects of LED lighting on residential demand:
That is an actual funded study of almost 900 homes that shows the continuous demand is going down.the treatment of the first 10 kW of load at 100% should be reduced to 8 kW at 100% based on analysis performed by LBNL on sub-metering data from 942 occupied US dwellings.