Now that we can view all the proposals I just came across this one Public Input No. 2407-NFPA 70-2023 from Generac of all people that proposed to treat EVSE loads differently in the residential Optional Calc.
A dwelling could have any number of large loads that run 3 hours or more and the optional calcs have historically taken that into account by where they set the demand factor cut off (10kw).
Mike has a different proposal 3204-NFPA 70-2023 [ Section No. 220.82(B) ]
That would lump EVSE's under B(3) and continue to allow the EVSE to be considered in the demand factor.
There are also a few other interesting proposals for 220.82 (and others in 220) such as 3239-NFPA 70-2023 [ Section No. 220.82(B) ]
from Lawrence Berkley National Labs (LBNL) that has been studying the effects of LED lighting on residential demand:
It is curious to me what is different about a EVSE load than any other residential continuous load?The 2023 version of NFPA 70 (NEC) article 220, Part VI - Optional Feeder and Service Load Calculations in article 220.82 Dwelling Unit, paragraphs (A), (B), and (C) currently do not specifically address the inclusion of EVSE equipment loads. This proposes a revision of article 220.82(A) to include adding a new paragraph (D) which is to include EVSE loads into the Optional Feeder and Service Load Calculation – This corresponds with Public Input No. 2282-NFPA 70-2023. Per 2023 NEC Article 220, Part III. Feeder and Service Load Calculations: • Article 220.53 Appliance Load – Dwelling Unit(s). This demand factor shall not apply to: (5) Electric Vehicle Supply Equipment (EVSE). • Article 220.57 Electric Vehicle Supply Equipment (EVSE) Load. The EVSE load shall be calculated at either 7200 watts (volt-amperes) or the nameplate rating of the equipment, whichever is larger.
That is an actual funded study of almost 900 homes that shows the continuous demand is going down.the treatment of the first 10 kW of load at 100% should be reduced to 8 kW at 100% based on analysis performed by LBNL on sub-metering data from 942 occupied US dwellings.