Mainly that 220.82 can be used for new construction that doesn't exist yet. 220.83 cannot.
The requirement is a bit more lenient in 220.83. You only have to count the first 8kVA (of non-heating/cooling load) at 100%, not the first 10kVA. And the requirements for consideration of heating and cooling are slightly different.