I'm trying to improve my understanding of the residential side of the NEC, and I recently came across 220.83, which can be used to determine whether or not an existing service is large enough to serve additional loads. My confusion is with part (A), which doesn't seem to include HVAC loads.
Am I to understand that, in the case of 220.83(A), HVAC units are to be counted as appliances? If that's the case, then ALL loads, including the new loads and the existing HVAC, are totaled up and counted at 100% for the first 8 kVA and at 40% for the remainder. Is this correct?
In this section I see general lighting/receptacle loads, SABCs, the required laundry circuit, and specific appliances. What I don't see is any mention of HVAC loads. Obviously, I'm missing something here, because there's no way we don't count existing heating and cooling loads just because no new ones are being installed.220.83 Existing Dwelling Unit.
...
(A) Where Additional Air-Conditioning Equipment or Electric Space-Heating Equipment Is Not to Be Installed. The following formula shall be used for existing and additional new loads.
____________Load (kVA)_______Percent of Load___________
First 8 kVA of load at...................................100
Remainder of load at.....................................40
Load calculations shall include the following:
(1) General lighting and general-use receptacles at 33 volt-amperes/m2 or 3 volt-amperes/ft2 as determined by 220.12
(2) 1500 volt-amperes for each 2-wire, 20-ampere small-appliance branch circuit and each laundry branch circuit covered in 210.11(C)(1) and (C)(2)
(3) The nameplate rating of the following:
.....a. All appliances that are fastened in place, permanently connected, or located to be on a specific circuit
.....b. Ranges, wall-mounted ovens, counter-mounted cooking units
.....c. Clothes dryers that are not connected to the laundry branch circuit specified in item (2)
.....d. Water heaters
Am I to understand that, in the case of 220.83(A), HVAC units are to be counted as appliances? If that's the case, then ALL loads, including the new loads and the existing HVAC, are totaled up and counted at 100% for the first 8 kVA and at 40% for the remainder. Is this correct?