So, what I'm thinking is you multiply the 1.58 times that multiplier of 60 which would give me 94.8KVA which would be about what I would expect in the dead of winter with 90kw of heat in the building.
Multiply that by 1.25 per 220.87 gives me 118.5KVA.
600 AMP 208 service = 216KVA
216 - 118.5 = 97.5KVA or 260 amps available.
Am I thinking right on this?