In a number of years inspecting, I have not actually has anyone use 220.87 for service calculations even though it seems to be one of the most accurate means. I am simply skeptical from lack of experience with that method.
I have an older hotel that was converted to muti-family dwellings. The ancient service was in poor condition and had a melt-down.
The original service had been tapped a number of times so there is really no "main" to reference.
There will be very limited load modifications when replacing the service. Past power bills showing demand are available. Is there any reason not to use them as noted in 220.87 to determine the new service size ?
I have an older hotel that was converted to muti-family dwellings. The ancient service was in poor condition and had a melt-down.
The original service had been tapped a number of times so there is really no "main" to reference.
There will be very limited load modifications when replacing the service. Past power bills showing demand are available. Is there any reason not to use them as noted in 220.87 to determine the new service size ?