Cell Phone Carrrier SIte ....Site has 5 meter loops on bussed wire trough. we are only able to acquire Peak Load from 1 site and getting remaining Peak loads from other carriers has been difficult. Customer wants generator to operate all five carriers at once during outage. Any suggestion on how to establish load for rest of equipment onsite? We could record readings for 30days but any suggestions on how to get information needed. All Carriers are aware of but not really cooperating.
 
Load should be stable other than heat/AC which you could kick on if you have access or just wait and clamp it. Probably very little need to do a 30 day, unless some authority wants it. These things dont draw much. Ours does 30 A on two out of three phases, 120/208, when the bard kicks in and that's most of the load. Maybe 10 on the other leg
 