winnie
- Springfield, MA, USA
- Electric motor research
I do see references 380/220 But i checked motors They have 380/220 380 high 220low
They all tapped for low?
The motors are designed to be connected in wye for 380V or in delta for 220V, and the equipment manufacturer could use either. You just need to match what the manufacturer configured things to be. The fact that there is an inverter involved is also an important clue; you need to match the voltage class of that inverter.
When a piece of equipment says it needs ' Power: 4P, 380/220V, 50/60Hz; ' I read that as requiring 380V L-L _and_ 220V L-N. But it might be the case that the machine really can use one or the other. All I have to go on is a spec on a web page probably translated from Chineese.
-Jon