Been doing apartment load calculations and was curious if anyone sees an issue using 220.84 over going through Part III of 220? I just compared the numbers and if I could save 38% using the method in 220.84.
220.84 Method
| General Wattage Total: | 194,400.0 | |
| 1st 3,000 @ 100% | 3,000.0 | Table 220.42 |
| 3,000 to 120,000 @ 35% | 42,000.0 | |
| Greater than 120,000 @25% | 18,600.0 | |
| Ranges | 192,000.0 | Table 220.61 |
| Ranges Diversified | 49,920.0 | |
| Dryers | 120,000.0 | Table 220.54 |
| Dryers Diversified | 41,400.0 | |
| Dishwashers | 33,600.0 | 220.53 |
| Dishwashers Diversified | 25,200.0 | |
| Water Heaters | 120,000.0 | |
| Water Heaters Diversified | 90,000.0 | |
| HVAC | 288,492.0 | |
| Elevator** | 0 | |
| Landlord RCPTS/Lighting | 26,000 | |
| LL Electric Heat | 0 | |
| Total: | 584,612 | watts |
| Amperage: | 1,623 | amps |
| Phase: | 3 | |
| Voltage: | 208 |
220.84 Method
| General Wattage Total: | 194,400.0 |
| Ranges | 192,000.0 |
| Dryers | 120,000.0 |
| Dishwashers | 33,600.0 |
| Water Heaters | 120,000.0 |
| HVAC | 288,492.0 |
| Total @ 100% | 948,492.0 |
| Total @ 36% | 341457.1 |
| Landlord Load | 26,000 |
| Total Load | 367457.1 |
| Amperage | 1020.714 |