I have a 220 volt car lift motor-single phase. It comes with a black, white and green grounding screw.
Question: I hook one hot wire to the black and the other to the white wire? Which I asume is not a neutral? And green to screw. Is that correct?
Which one?Since when do they let Diyers post on here?
Reidentify the white and away you go.
NEC does not apply to what motor manufacturer uses for their leads.
There are many 4,9,12, or more lead motors out there with all leads white and we do not re-identify these.
NEC does not apply to what motor manufacturer uses for their leads.
There are many 4,9,12, or more lead motors out there with all leads white and we do not re-identify these.
This is true but it's more of a cya for the next person who may work on it.