I need to put a number on the install of two 72kw 480V 3? steam generators.
Here's what I have.
72000?830=86.7A
86.7?1.25=108A
So lets say 110A ?2=220A
I have one 200A frame left in the 480 gear.
Thank you.
Is there something in 220 or 422 that would alow this install? Both generators will be on 24/7.