CCCI
Member
- Location
- Orlando, Florida
I need to hook up a 220 volt motor to 208 volts. I believe that this would be fine because it is in the 10% area of the voltage. I'm I looking at this right?This is for a 1 1/2 HP drill press.
CCCI said:The nameplate has 110/220V and the motor has a big sticker that says, "Pre wired 220 volts"
It also has a wiring diagram that has the 220v wiring in the owners manual and an NEMA 6-15 plug on the cord.
Buddy, I was trying to do the lead in for "220... 221 ~ whatever it takes.":wink:kbsparky said:European systems' nominal voltage can be 220/380 Volts.
Mr. Mom.e57 said:Buddy, I was trying to do the lead in for "220... 221 ~ whatever it takes.":wink:
e57 said:What system delivers 220 anyway?
CCCI said:I just found out that it was made in Taiwan that has a 110/220 volt system. We have 209.5 volts at the location that it will be hooked up at.
Motor terminal voltage with panel of 234, 200 ft of #14, 10A load, plug and cord connected ... very realistic. If you look on Baldor's website, they have single phase motors rated at 110/220, 115/230, and 115/208-230. I find the voltage selections interesting with 208 being sqrt(3) related to 120, not 115 ...e57 said:What system delivers 220 anyway?
GeorgeB said:Motor terminal voltage with panel of 234, 200 ft of #14, 10A load, plug and cord connected ... very realistic. If you look on Baldor's website, they have single phase motors rated at 110/220, 115/230, and 115/208-230. I find the voltage selections interesting with 208 being sqrt(3) related to 120, not 115 ...
Ah well.