220V Twist Lock

Status
Not open for further replies.

Langd0

Member
Location
Derby, UK
Hi,

What plug would you expect to be used for a 220V 3 phase system with no neutral (<10A per phase)? L15-20? L18-20?

Then the same question but with a neutral as well?

Cheers

Ryan
 
It appears you are in the UK, so we’ll give you a pass... :p

It will have to start with whether your equipment is “double insulated”, or needs a ground pin.
 
From the NEMA chart Larry posted:

Three pole 220 (208 to 250) Volts with ground, L15-20.

As above, but with Neutral, a 5 wire cord, L21-20.

You can use the 30 amp twist locks if you wish.

There are older non-NEMA twist locks still out there, do not use them for new installations of new equipment. Like those L18-20, which are three pole with neutral, NO GROUND! We have building here with those installed, using the silver screws connected to ground, not a neutral. I have replaced the ones I come across with L15-20., just to keep green Green!:thumbsup:
 
It appears you are in the UK, so we’ll give you a pass... :p

It will have to start with whether your equipment is “double insulated”, or needs a ground pin.

If in UK, isn't it likely that we have 415V wye? Thus 220 (or 240 or whatever we want to call it) phase to neutral? I'd want a little more info to make a recommendation.
 
All passes greatly received!

Sorry, I took the earth for granted. I need a 4 wire (3 phase and earth) plug for 220V and a 5 wire (3 phase, neutral and earth) plug for 127/220V supply, with current less than 10A per phase.

I guess basically what I'm asking is does the 208V quoted voltage of the L21-20P prevent the use of it on a 220V supply?

Does the quoted voltage of 250V of the L15-20 prevent the use of it on a 220V supply?

Designing equipment to go to South America in this instance - not the UK!

Cheers
 
I guess basically what I'm asking is does the 208V quoted voltage of the L21-20P prevent the use of it on a 220V supply?
Does the quoted voltage of 250V of the L15-20 prevent the use of it on a 220V supply?

The parts are made of the same material, so it's a question of what the user expects. The L21 is intended for 120V to ground, not 208V (that's phase-to-phase), so that would be a poor choice. With the L15 being spec'd for 250V to ground, using only 220V wouldn't be a problem unless someone connects your 220V equipment to a 250V supply.

Unless the target country uses the NEMA connector styles, you're probably better off with an IEC pin&sleeve connector, looks like the 516P6W would do the trick (https://www.stayonline.com/reference-iec309-international.aspx).
 