220volt motor with 480 VSD

Status
Not open for further replies.
B

bthielen

Guest
Re: 220volt motor with 480 VSD

What would be the full load amps
Should be able to find this information on the motor nameplate. You will still be using it in a 220v application.
 

tom baker

First Chief Moderator
Staff member
Re: 220volt motor with 480 VSD

Yes it can be done, if the VFD is large enough.
You'll need to review the manual for the VFD.
Amps are determined by HP and voltage. Check the nameplate.
 