Reading This. It says for 1
10 feet above finished grade, sidewalks, platforms, or projections from which they might be accessible to pedestrians if circuits are 150V to ground or less.
2 states
I have a Killer hill drop that is overhead and my 20 mast that feeds a barn down in a ditch I can't get past 10'. It is a Resident. It is also Finish grade. Number 1 does not care if its reidential, Commerical, or industrial. As long as its not over 150v to ground 10' is the mark.
What inspector says is 12 feet does say Residential property but adds the not over 300v to ground.
This is 120/240 volt system.
Its only 120 volts to ground. I say 10' works what do you say.
10 feet above finished grade, sidewalks, platforms, or projections from which they might be accessible to pedestrians if circuits are 150V to ground or less.
2 states
- 12 feet above residential property and driveways, and commercial areas not subject to truck traffic if circuits of 300V to ground or less. It's 15 feet for circuits over 300V to ground.
I have a Killer hill drop that is overhead and my 20 mast that feeds a barn down in a ditch I can't get past 10'. It is a Resident. It is also Finish grade. Number 1 does not care if its reidential, Commerical, or industrial. As long as its not over 150v to ground 10' is the mark.
What inspector says is 12 feet does say Residential property but adds the not over 300v to ground.
This is 120/240 volt system.
Its only 120 volts to ground. I say 10' works what do you say.