A/A Fuel GTX Senior Member Location WI & AZ Occupation Electrician Jul 5, 2011 #1 Does 225.19 apply to service entrance conductors also or is that a POCO issue?
iwire Moderator Staff member Location Massachusetts Jul 5, 2011 #2 A/A Fuel GTX said: Does 225.19 apply to service entrance conductors also or is that a POCO issue? Click to expand... Nothing in 225 applies to service conductors. There are height requirements for service conductors in Article 230. See 230.24 for a start. BUT ..... nothing in the NEC applies on the power company side of the service point. See 90.2(B)(5)(a)
A/A Fuel GTX said: Does 225.19 apply to service entrance conductors also or is that a POCO issue? Click to expand... Nothing in 225 applies to service conductors. There are height requirements for service conductors in Article 230. See 230.24 for a start. BUT ..... nothing in the NEC applies on the power company side of the service point. See 90.2(B)(5)(a)