Does 225.19 apply to service entrance conductors also or is that a POCO issue?

Nothing in 225 applies to service conductors.

There are height requirements for service conductors in Article 230. See 230.24 for a start.


BUT ..... nothing in the NEC applies on the power company side of the service point.

See 90.2(B)(5)(a)
 