Can you have a 208/120V service into a building and also have a 480/277V feeder from a separate building? My instincts say no, but I don't see the words that say no in either article.
Certainly you can, as those two supplies are different voltages, and both 225.30 and 230.2 have allowances for multiple supplies of different characteristics.Can you have a 208/120V service into a building and also have a 480/277V feeder from a separate building? My instincts say no, but I don't see the words that say no in either article.
No. Each serves a mechanical pump. There are no 700 loads other than egress lights.Are the branch circuits an emergency source?
If both feeders originate in the same supply equipment in building 1, then it is allowed under 2020 and 2023 NEC 225.30(B) (which allowance is not present in earlier NECs). Likewise, if both branch circuits originate in the same supply equipment in building 2, that it is allowed under the same section.However, this project's designer has some other rethinking to do. It's not just one 480V feeder from bldg 1 to bldg 2, but two such feeders. Also, there are 2 branch circuits from bldg 2 back to bldg 1.
That is essentially the same issue that I am hoping to resolve here. Two voltages are OK, but is one service plus one feeder also OK?The more interesting question is whether you can have a 208Y/120V service into a building and also a 280Y/120V feeder from a separate building. 230.2 refers only to the number of services, and 225.30 refers only to the number of branch circuit and feeders. So it appears that any building can have 1 supply of each tytype.
I had this same issue come up on me many moons ago and I submitted the question to NC yearly conference on the code. The panel is made up of some big wigs from the nec cmp.The more interesting question is whether you can have a 208Y/120V service into a building and also a 280Y/120V feeder from a separate building. 230.2 refers only to the number of services, and 225.30 refers only to the number of branch circuit and feeders. So it appears that any building can have 1 supply of each type.
Yes, there is no language prohibiting it. Article 230 covers the numbers of services; Article 225 covers the number of branch circuits and feeders; and there's nothing in either article that would case one to affect the other.That is essentially the same issue that I am hoping to resolve here. Two voltages are OK, but is one service plus one feeder also OK?
In our situation we had a detached garage that had a service feeding the garage apt on the second floor but the actual feeder for the garage itself came from the existing house ,I had this same issue come up on me many moons ago and I submitted the question to NC yearly conference on the code. The panel is made up of some big wigs from the nec cmp.
The decision, as I recollect, was that it was compliant
Can you have a 208/120V service into a building and also have a 480/277V feeder from a separate building? My instincts say no, but I don't see the words that say no in either article.
...
Amazingly all the PIs were rejected, and the panel statements in the rejections did not even comment on the underlying question. It appeared the CMP in charge of 225 would not even comment on services, and the CMP in charge of 230 would not even comment on feeders or branch circuits. So there is nobody to address the question of how the two articles interact with respect to supplying a building.
...
I would say yes with grouping of the disconnects...Theoretical comparison:
Suppose you had, say, four condominiums that share a single, detached, four-car parking garage.
Could each parking bay be supplied with a light and receptacle from the owners' respective units?