I was wandering if the company I work for is in compliance with this 225.30 code which says:
A building or structure that is served by a branch circuit or feeder on the load side of a service disconnect means shall be supplied by only one feeder or branch circuit unless permitted by 250.30 A through E
B) common supply feeder where the feeder conductors originate in the same panel board, switchgear or OTHER DISTRIBUTION equipment and each feeder terminates in a single disconnect means, not more than SIX FEEDERS shall be permitted
Therefore, if our company has a utility substation feeding power pole lines 4800 volts to a company owner pad mounted transformer Delta Delta 3 phase ungrounded system stepping down to 480 volts AC as the separately derived system.
This separately derived system secondary conductors terminate to a single vault or room mounted disconnect
From this one disconnect a single feeder terminates to a panel with 3 buss bars for terminating taps going to 3 separate buildings and a trailer for motor control which are all about 100 to 200 feet away (tapped runs without OCPD on line side of taps)
The three buildings and trailer each have a sub panel where they receive their feeder and disconnect means
My question is does this set up meet the requirements for up to 6 feeders (and disconnects) from a single distribution bus panel explained before or aren’t the disconnects required to be bundled together near the tap distribution panel and labeled with a directory for its purpose instead of just terminating each tap feeder to each building in a sub panel? and does this tap distribution panel qualify as “feeders originating in the same distribution equipment?”
A building or structure that is served by a branch circuit or feeder on the load side of a service disconnect means shall be supplied by only one feeder or branch circuit unless permitted by 250.30 A through E
B) common supply feeder where the feeder conductors originate in the same panel board, switchgear or OTHER DISTRIBUTION equipment and each feeder terminates in a single disconnect means, not more than SIX FEEDERS shall be permitted
Therefore, if our company has a utility substation feeding power pole lines 4800 volts to a company owner pad mounted transformer Delta Delta 3 phase ungrounded system stepping down to 480 volts AC as the separately derived system.
This separately derived system secondary conductors terminate to a single vault or room mounted disconnect
From this one disconnect a single feeder terminates to a panel with 3 buss bars for terminating taps going to 3 separate buildings and a trailer for motor control which are all about 100 to 200 feet away (tapped runs without OCPD on line side of taps)
The three buildings and trailer each have a sub panel where they receive their feeder and disconnect means
My question is does this set up meet the requirements for up to 6 feeders (and disconnects) from a single distribution bus panel explained before or aren’t the disconnects required to be bundled together near the tap distribution panel and labeled with a directory for its purpose instead of just terminating each tap feeder to each building in a sub panel? and does this tap distribution panel qualify as “feeders originating in the same distribution equipment?”