225.30 violation or not

Status
Not open for further replies.

RUWired

Senior Member
Location
Pa.
Multiple branch circuits running through light bases ( spliced through at hand hole). 2 seperate circuits ( 480 volt heads )required at each base for reliability and 2 other circuits passing through to pick up other light bases.I take it as a light base is a structure.
Rick
 
This would be on a multi building facility, but does that apply to branch circuits? It is a requirement to apply l.o.t.o. before working on any circuit.
 
RUWired said:
Multiple branch circuits running through light bases ( spliced through at hand hole). 2 seperate circuits ( 480 volt heads )required at each base for reliability and 2 other circuits passing through to pick up other light bases.I take it as a light base is a structure.
Rick

Are you concerned about having two circuits feeding each pole, or about the other circuits which feed through them?
 
crossman said:
Are you concerned about having two circuits feeding each pole, or about the other circuits which feed through them?
My concern is both. The safety concern is no different than a j-box with multiple circuits. Is a concrete base a seperate structure and would 225.30 apply? If it is allowed, would a ground rod then be required?( 250.32(A) )
 
IMO there is no question a light pole or sign pylon are structures to the NEC and require disconnecting means per 225.31.

However Exception 3 and 4 to 225.32 allow these required disconnecting means to be located elsewhere.

If you have multiple circuits supplying the pole then you need a grounding electrode per 250.32(A). Keep in mind a multiwire branch circuit can be called one circuit.
 
RUWired said:
My concern is both. The safety concern is no different than a j-box with multiple circuits. Is a concrete base a seperate structure and would 225.30 apply? If it is allowed, would a ground rod then be required?( 250.32(A) )

Don't the poles have a ufer/ground wire in the concrete base?
 