Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The engineering firm wants to run lighting and receptacle circuits (120/208V) from a remote location Panelboard into a separate building without a disconnecting means for the circuits where they enter the building -
Is this code compliant ?


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree with tom but you might note there are exceptions to 225.32. Generally not applicable but there are situations,.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Exception 1 seems to allow it. What’s your interpretation ?


Sent from my iPhone using Tapatalk
What code cycle are you under. Before the 2020 you couldn't run more than a single circuit to a remote structure. How many circuits are they proposing to run
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
What code cycle are you under. Before the 2020 you couldn't run more than a single circuit to a remote structure. How many circuits are they proposing to run

2020. They’re running 3 circuits at 208V
ABC neutral and ground


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It seems somewhat clear-cut.
In order to circumvent the disconnect requirement the facility would need to meet all the criteria in the exception. IMO this would require full time personnel and written LOTO such as at am industrial facility,.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I agree with tom but you might note there are exceptions to 225.32. Generally not applicable but there are situations,.
I answered too fast, generally no.
And per the previous post probably not
For 3, 3 phase circuits, it would be easier to run a feeder
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
2020. They’re running 3 circuits at 208V
ABC neutral and ground
You're in luck. A MWBC is considered a single circuit in this case.

Wait: Is that three or nine circuits? One MWBC or three MWBCs?

Electrically speaking, a feeder is more efficient than individual circuits.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
It seems somewhat clear-cut.
In order to circumvent the disconnect requirement the facility would need to meet all the criteria in the exception. IMO this would require full time personnel and written LOTO such as at am industrial facility,.

The exception will probably apply since it’s an industrial faculty with qualified electricians on site - they’ll argue they have a LOTO. But it’s poor design in my opinion


Sent from my iPhone using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The exception will probably apply since it’s an industrial faculty with qualified electricians on site - they’ll argue they have a LOTO. But it’s poor design in my opinion


Sent from my iPhone using Tapatalk


I agree the exception may work but make sure they label where the the multiwire branch circuit is fed from. A 3 pole disconnect where the wiring hits the building would be a simple install and easier, IMO then doing permanent marking of where the breaker is in another building.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I agree the exception may work but make sure they label where the the multiwire branch circuit is fed from. A 3 pole disconnect where the wiring hits the building would be a simple install and easier, IMO then doing permanent marking of where the breaker is in another building.

Agreed completely! Thanks to all


Sent from my iPhone using Tapatalk
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
For 120 v mwbc it’s a snap switch.
Is a 3 pole snap switch available?
Absolutely.