225.31

Status
Not open for further replies.

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
YES OR NO?

225.31 Disconnecting Means. Means shall be provided
for disconnecting all ungrounded conductors that supply or
pass through the building or structure.

Attached? Detached?

threebuildings.jpg
 
I would check with the building code but around here if it has a roof attaching the buildings it is attached. Obviously not an NEC issue on this ruling.
 
Could be under older codes. 3-wire or 4-wire?
The NEC never made conditions to determine if a building was detached or attached. This is strictly a building code issue or building department judgement call. If it was built prior to the 2008 NEC then 3 wire was all that was required if there were no metal pathways common to the buildings. Otherwise 4 wire is required if there is a feeder.
 
The NEC never made conditions to determine if a building was detached or attached. This is strictly a building code issue or building department judgement call. If it was built prior to the 2008 NEC then 3 wire was all that was required if there were no metal pathways common to the buildings. Otherwise 4 wire is required if there is a feeder.

Correct. Making the point that you need to know how the structure is treated before you wire it.

What if these were three seperate structures. Could you have 3 ways 'in' different buildings serve the covered areas? Could the three ways be on the outside of the structure?
 
Correct. Making the point that you need to know how the structure is treated before you wire it.

What if these were three seperate structures. Could you have 3 ways 'in' different buildings serve the covered areas? Could the three ways be on the outside of the structure?

Check out 225.36 Exception
 