I am pondering the case of additional feeders between buildings and where the disconnects need to be located.
Simple right?
Say for example in my case two 'additional' feeders, a parallel power production and an optional standby generator feeder as permitted in 225.30(A)(4) and (5). The building call it building 'B' is supplied by a primary feeder from another building, Building 'A'. Building 'A' contains the service point.
The two additional feeders between buildings have the source and supply reversed with respect to the service point.
So how is 225.32 and thus the referenced 230.6 interpreted when the feeder travels a distance from the source inside the building 'B' then exits to its destination building 'A'?
Is the 230.6 'nearest the point of entrance' the feeder source at building 'B', I.E the generator or inverter?
Or is the 230.6 'nearest the point of entrance' where the feeder 'exits' building 'B' heading say underground towards building 'A' the service point.
Thoughts? Opinions?
Thanks in advance.
Simple right?
Say for example in my case two 'additional' feeders, a parallel power production and an optional standby generator feeder as permitted in 225.30(A)(4) and (5). The building call it building 'B' is supplied by a primary feeder from another building, Building 'A'. Building 'A' contains the service point.
The two additional feeders between buildings have the source and supply reversed with respect to the service point.
So how is 225.32 and thus the referenced 230.6 interpreted when the feeder travels a distance from the source inside the building 'B' then exits to its destination building 'A'?
Is the 230.6 'nearest the point of entrance' the feeder source at building 'B', I.E the generator or inverter?
Or is the 230.6 'nearest the point of entrance' where the feeder 'exits' building 'B' heading say underground towards building 'A' the service point.
Thoughts? Opinions?
Thanks in advance.