- Lockport, IL
- Semi-Retired Electrical Engineer
A small building, remote from the main building, needs 120 volt power for receptacles and for lights. I reviewed the design and noted that it called for two separate circuits to be run from a panel in the main building. It also had two separate disconnect switches on the outside of the small building. I pointed out to the designer that 225.30 would not allow two branch circuits, and that a MWBC would be needed. I know that we will need to do something with the building's required disconnecting means. I see that 225.33(B) allows two separate single pole disconnects to serve this function. But how do we handle the shared neutral? Here is what I am thinking:
- From a two-pole breaker on the branch panel, run one conduit to the first disconnect, with both ungrounded conductors, the shared neutral, and the shared EGC.
- Tap the neutral, and run it, along with the ungrounded conductor on the load side of the disconnect, to the receptacle loads.
- Run the other ungrounded conductor, along with the tapped neutral, to the other disconnect switch, to serve the lighting loads.
- Provide a listed handle tie between the two disconnect handles.