I'm probably splitting hairs here. I have a generator, ats, fusible service switch all more than 50' from a building. I need the disconnect specified by 225.31 and 225.36. all references are NEC2008. defiinition of service equipment contains test "usually consisting of a circuit breaker . . . . ".
In my application where I have either the service disconnect or generator breaker providing the overcurrent protection, can I simply install a switch without fuses as the building disconnect. design included mcb panelboard but mlo panelboard has already been ordered.
must service equipment (not service entrance rated) contain overcurrent protection?
Thanks,